I am trying to connect to EDMI Mk10M DLMS meter however every time i get the error "ParseObjects failed. Invalid parameter" when trying to refresh the objects list. Please see an image attached, what could possibly cause this issue? Thank you
The meter returns an error. Can you read the association view with authentication level None?
It might be that the association view is not implemented for this association.
Please add text in the future, not pictures. It's easier to read hex from the text.
Apologies for posting a picture instead of pure text, this is what i get with the none authentication level and as soon as i select yes on association view... i tried different baud rates, but still not able to complete the process. Please see the logs below :
A quick update, i managed to get past "failed to reply from the device at given time" error after increasing the number of tries. The issue now is the read-write error, please see below, sorry for the long logs.
There are lots of objects where only the logical name is implemented and there is no other data. For example, register object 1.0.21.8.0.255. There is an access right only for the logical name.
The client application tries to read those values and you get a read-write denied error because of that.
The client application reads all the objects from the meter. You can read only values that you need and that are implemented for the meter. You can also ask if there is new firmware available for the meter where those objects are implemented.
Hi Miko,
Hi Miko,
15:26:00 Initializing serial connection.
15:26:01 Send SNRM request.
7E A0 08 02 23 21 93 BD 64 7E
15:26:01
7E A0 21 21 02 23 73 8F 72 81 80 14 05 02 03 00 06 02 08 00 07 04 00 00 00 01 08 04 00 00 00 01 3F 05 7E
15:26:01 Parsing UA reply succeeded.
15:26:01 Send AARQ request.
7E A0 2C 02 23 21 10 AF 9F E6 E6 00 60 1D A1 09 06 07 60 85 74 05 08 01 01 BE 10 04 0E 01 00 00 00 06 5F 1F 04 00 00 1E 5D FF FF B3 E2 7E
15:26:01
7E A0 38 21 02 23 30 34 E7 E6 E7 00 61 29 A1 09 06 07 60 85 74 05 08 01 01 A2 03 02 01 00 A3 05 A1 03 02 01 00 BE 10 04 0E 08 00 06 5F 1F 04 00 00 10 10 08 00 00 07 02 74 7E
15:26:01 Parsing AARE reply succeeded.
15:26:03 --- Collecting objects. ---
15:26:03 Collecting objects
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 02 00 91 53 7E
15:26:04
7E A3 19 21 02 23 52 88 C0 E6 E7 00 C4 02 C1 00 00 00 00 01 00 82 03 00 01 82 02 5F 02 04 12 00 01 11 00 09 06 00 00 2A 00 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 04 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 05 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 02 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 05 60 01 03 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 04 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 04 05 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 04 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 04 06 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 02 08 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 60 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 2B 01 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 2B 01 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 64 60 00 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 64 60 00 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 64 60 00 04 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 64 60 00 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 61 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 61 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 61 02 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 4A 8B 7E
15:26:04 Get Next Data block.
15:26:04 Collecting objects
7E A0 14 02 23 21 54 7E 15 E6 E6 00 C0 02 C1 00 00 00 01 51 BE 7E
15:26:05
7E A3 19 21 02 23 74 BC 84 E6 E7 00 C4 02 C1 00 00 00 00 02 00 82 03 00 06 00 01 60 07 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 01 60 0F 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 0C 20 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 0C 24 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 62 81 06 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 94 03 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 62 81 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 62 81 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 62 81 04 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 62 81 05 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 94 02 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 94 01 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 62 81 08 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 62 81 09 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 07 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 08 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 09 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 0A FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 88 00 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 88 00 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 88 00 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 88 00 04 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 88 00 05 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 62 01 80 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 0B FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 94 00 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 38 AC 7E
15:26:05 Get Next Data block.
15:26:05 Collecting objects
7E A0 14 02 23 21 76 6E 17 E6 E6 00 C0 02 C1 00 00 00 02 CA 8C 7E
15:26:06
7E A3 19 21 02 23 96 A0 40 E6 E7 00 C4 02 C1 00 00 00 00 03 00 82 03 00 00 02 04 12 00 01 11 00 09 06 00 64 60 00 05 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 64 60 00 06 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 64 60 00 62 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 64 60 00 63 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 0C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 64 60 00 07 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 64 60 00 08 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 0D FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 05 60 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 05 61 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 0E FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0A 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0A 02 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0A 03 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 61 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 0A FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 14 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 0B FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 15 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0B 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0B 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0B 02 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0B 04 FF 02 02 01 7A 78 7E
15:26:06 Get Next Data block.
15:26:06 Collecting objects
7E A0 14 02 23 21 98 1E 19 E6 E6 00 C0 02 C1 00 00 00 03 43 9D 7E
15:26:07
7E A3 19 21 02 23 B8 DC 88 E6 E7 00 C4 02 C1 00 00 00 00 04 00 82 03 00 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0B 05 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0B 06 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 0C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 61 62 16 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 94 09 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 64 60 00 0A FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 64 60 00 0B FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 64 60 00 0C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 8C 00 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 8C 00 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 94 02 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 8C 00 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 0F FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 10 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 11 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 12 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 13 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 14 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 07 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 16 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 17 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 18 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 0C 05 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 19 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 00 A3 7E
15:26:07 Get Next Data block.
15:26:07 Collecting objects
7E A0 14 02 23 21 BA 0E 1B E6 E6 00 C0 02 C1 00 00 00 04 FC E9 7E
15:26:08
7E A3 19 21 02 23 DA C8 C8 E6 E7 00 C4 02 C1 00 00 00 00 05 00 82 03 00 12 00 01 11 00 09 06 00 00 83 00 1A FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 1B FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 0F 24 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 0B 24 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 1C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 1D FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 60 01 06 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 1E FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 1F FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 20 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 02 01 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 21 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 22 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 23 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 24 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 25 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 26 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 27 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 28 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 29 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 2A FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 83 00 2C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 01 11 00 09 06 01 00 00 0B 07 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 94 0A 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 01 11 00 09 06 00 00 94 0B 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 7F 87 7E
15:26:08 Get Next Data block.
15:26:08 Collecting objects
7E A0 14 02 23 21 DC 3E 1D E6 E6 00 C0 02 C1 00 00 00 05 75 F8 7E
15:26:09
7E A3 19 21 02 23 FC FC 8C E6 E7 00 C4 02 C1 00 00 00 00 06 00 82 03 00 02 04 12 00 01 11 00 09 06 00 00 83 00 2D FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 00 11 00 09 06 E8 B1 FF 1F 35 C8 02 02 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 15 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 29 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 3D 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 09 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 16 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 2A 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 3E 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 09 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 10 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 17 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 2B 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 3F 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 09 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 18 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 2C 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 40 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 09 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 80 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 19 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 2D 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 41 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 1A B2 86 7E
15:26:09 Get Next Data block.
15:26:09 Collecting objects
7E A0 14 02 23 21 FE 2E 1F E6 E6 00 C0 02 C1 00 00 00 06 EE CA 7E
15:26:10
7E A3 19 21 02 23 1E E0 48 E6 E7 00 C4 02 C1 00 00 00 00 07 00 82 03 00 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 2E 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 42 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 1B 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 2F 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 43 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 1C 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 30 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 44 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 1D 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 31 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 45 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 1E 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 32 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 46 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 04 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 04 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 05 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 05 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 06 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 06 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 07 FF 02 02 01 01 02 03 0F 01 16 08 1B 7E
15:26:10 Get Next Data block.
15:26:10 Collecting objects
7E A0 14 02 23 21 10 5E 11 E6 E6 00 C0 02 C1 00 00 00 07 67 DB 7E
15:26:11
7E A3 19 21 02 23 30 9C 80 E6 E7 00 C4 02 C1 00 00 00 00 08 00 82 03 00 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 07 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 08 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 08 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 09 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 09 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 0A FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 0A FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 0B FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 0B FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 0C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 0C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 0D FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 0D FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 0E FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 0E FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 0F FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 0F FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 10 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 10 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 11 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 11 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 12 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 12 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 13 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 13 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 14 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 14 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 3B 20 7E
15:26:11 Get Next Data block.
15:26:11 Collecting objects
7E A0 14 02 23 21 32 4E 13 E6 E6 00 C0 02 C1 00 00 00 08 90 23 7E
15:26:12
7E A3 19 21 02 23 52 88 C0 E6 E7 00 C4 02 C1 00 00 00 00 09 00 82 03 00 06 01 00 01 08 15 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 15 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 16 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 16 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 17 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 17 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 01 08 18 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 08 18 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 04 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 04 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 05 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 05 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 06 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 06 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 07 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 07 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 08 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 08 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 09 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 09 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 0A FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 0A FF 02 02 01 01 02 38 5D 7E
15:26:12 Get Next Data block.
15:26:12 Collecting objects
7E A0 14 02 23 21 54 7E 15 E6 E6 00 C0 02 C1 00 00 00 09 19 32 7E
15:26:17 Failed to receive reply from the device in given time.
System.Exception: GetObjects failed. Failed to receive reply from the device in given time.
at GXDLMSDirector.MainForm.RefreshDevice(GXDLMSMeter dev, Boolean bRefresh)
at GXDLMSDirector.MainForm.Refresh(Object sender, GXAsyncWork work, Object[] parameters)
15:28:08 Send Keep Alive
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 0F 00 00 28 00 00 FF 01 00 F9 79 7E
15:28:13 Failed to receive reply from the device in given time.
15:28:13 Disconnect request
7E A0 08 02 23 21 53 B1 A2 7E
15:28:13
7E A0 08 21 02 23 1F 10 EA 7E
at GXDLMSDirector.GXDLMSCommunicator.ReadDataBlock(Byte[] data, String text, Int32 multiplier, Int32 tryCount, GXReplyData reply)
at GXDLMSDirector.GXDLMSCommunicator.ReadDataBlock(Byte[] data, String text, Int32 multiplier, GXReplyData reply)
at GXDLMSDirector.GXDLMSCommunicator.ReadDataBlock(Byte[] data, String text, GXReplyData reply)
at GXDLMSDirector.GXDLMSCommunicator.KeepAlive()
at GXDLMSDirector.GXDLMSDevice.KeepAlive_Elapsed(Object sender, ElapsedEventArgs e)
15:36:49
15:37:00 Initializing serial connection.
15:37:01 Send SNRM request.
15:37:01
15:37:01 Parsing UA reply succeeded.
15:37:01 Send AARQ request.
15:37:01
15:37:01 Parsing AARE reply succeeded.
15:37:03 --- Collecting objects. ---
15:37:03 Collecting objects
15:37:04
15:37:04 Get Next Data block.
15:37:04 Collecting objects
15:37:05
15:37:05 Get Next Data block.
15:37:05 Collecting objects
15:37:06
15:37:06 Get Next Data block.
15:37:06 Collecting objects
15:37:07
15:37:07 Get Next Data block.
15:37:07 Collecting objects
15:37:08
15:37:08 Get Next Data block.
15:37:08 Collecting objects
15:37:09
15:37:09 Get Next Data block.
15:37:09 Collecting objects
15:37:10
15:37:10 Get Next Data block.
15:37:10 Collecting objects
15:37:11
15:37:11 Get Next Data block.
15:37:11 Collecting objects
15:37:12
15:37:12 Get Next Data block.
15:37:12 Collecting objects
15:37:17 Data send failed. Try to resend 1/2
15:37:18
7E A3 19 21 02 23 74 BC 84 E6 E7 00 C4 02 C1 00 00 00 00 0A 00 82 03 00 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 0B FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 0B FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 0C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 0C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 0D FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 0D FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 0E FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 0E FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 0F FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 0F FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 10 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 10 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 11 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 11 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 12 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 12 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 13 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 13 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 14 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 14 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 15 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 15 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 16 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 16 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 17 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 08 17 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 08 18 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 D3 6E 7E
15:37:18 Get Next Data block.
15:37:18 Collecting objects
7E A0 14 02 23 21 76 6E 17 E6 E6 00 C0 02 C1 00 00 00 0A 82 00 7E
15:37:23 Data send failed. Try to resend 1/2
15:37:24
7E A3 19 21 02 23 96 A0 40 E6 E7 00 C4 02 C1 00 00 00 00 0B 00 82 03 00 03 11 00 09 06 01 00 04 08 18 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 04 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 04 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 05 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 05 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 06 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 06 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 07 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 07 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 08 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 08 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 09 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 09 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 0A FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 0A FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 0B FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 0B FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 0C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 0C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 0D FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 0D FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 0E FF 02 CD 65 7E
15:37:24 Get Next Data block.
15:37:24 Collecting objects
7E A0 14 02 23 21 98 1E 19 E6 E6 00 C0 02 C1 00 00 00 0B 0B 11 7E
15:37:25
7E A3 19 21 02 23 B8 DC 88 E6 E7 00 C4 02 C1 00 00 00 00 0C 00 82 03 00 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 0E FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 0F FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 0F FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 10 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 10 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 11 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 11 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 12 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 12 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 13 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 13 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 14 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 14 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 15 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 15 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 16 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 16 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 17 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 17 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 18 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 18 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 15 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 29 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 3D 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 16 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 2A 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 3E 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 12 95 7E
15:37:25 Get Next Data block.
15:37:25 Collecting objects
7E A0 14 02 23 21 BA 0E 1B E6 E6 00 C0 02 C1 00 00 00 0C B4 65 7E
15:37:26
7E A3 19 21 02 23 DA C8 C8 E6 E7 00 C4 02 C1 00 00 00 00 0D 00 82 03 00 02 04 12 00 03 11 00 09 06 01 00 01 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 02 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 17 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 2B 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 3F 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 18 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 2C 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 40 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 03 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 04 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 1D 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 31 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 45 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 1E 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 32 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 46 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 21 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 35 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 49 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0D 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 20 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 34 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 48 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 5C 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 1F 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 33 23 1B 7E
15:37:26 Get Next Data block.
15:37:26 Collecting objects
7E A0 14 02 23 21 DC 3E 1D E6 E6 00 C0 02 C1 00 00 00 0D 3D 74 7E
15:37:27
7E A3 19 21 02 23 FC FC 8C E6 E7 00 C4 02 C1 00 00 00 00 0E 00 82 03 00 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 47 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 5B 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 06 03 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 06 0B FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0E 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0C 1F 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0C 21 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0C 23 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0C 25 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 20 07 7C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 34 07 7C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 48 07 7C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0C 07 7C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 1F 07 7C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 33 07 7C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 47 07 7C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0B 07 7C FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 1F 07 7D FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 33 07 7D FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 47 07 7D FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0B 07 7D FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 09 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0A 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 22 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 36 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 4A 07 00 FF 02 02 01 01 02 03 0F 01 16 8B F9 7E
15:37:27 Get Next Data block.
15:37:27 Collecting objects
7E A0 14 02 23 21 FE 2E 1F E6 E6 00 C0 02 C1 00 00 00 0E A6 46 7E
15:37:28
7E A3 19 21 02 23 1E E0 48 E6 E7 00 C4 02 C1 00 00 00 00 0F 00 82 03 00 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 51 07 28 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 51 07 33 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 51 07 3E FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 51 07 01 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 51 07 02 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 51 07 15 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 51 07 2D FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 51 07 2E FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 51 07 38 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 05 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 06 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 07 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 08 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 60 09 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0F 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 10 08 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 83 00 0F FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 83 00 10 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 83 00 11 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 83 00 12 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 83 00 13 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0F 23 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0B 23 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 5A 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 0F 07 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 83 00 14 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 00 00 83 00 15 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 62 9F 7E
15:37:28 Get Next Data block.
15:37:28 Collecting objects
7E A0 14 02 23 21 10 5E 11 E6 E6 00 C0 02 C1 00 00 00 0F 2F 57 7E
15:37:29
7E A3 19 21 02 23 30 9C 80 E6 E7 00 C4 02 C1 00 00 00 00 10 00 82 03 00 06 00 00 83 00 2B FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 00 09 0B FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 03 11 00 09 06 01 00 00 03 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 01 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 02 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 03 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 04 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 09 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0A 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 01 06 01 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 02 06 01 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 01 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 02 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 01 06 03 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 02 06 03 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 01 06 04 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 02 06 04 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 01 06 05 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 02 06 05 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 01 06 06 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 02 06 06 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 01 06 07 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 02 06 07 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 01 06 08 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 02 06 08 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 03 06 01 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 04 06 01 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 03 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 04 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 03 06 03 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 04 06 03 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 03 06 04 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 04 06 04 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 03 06 05 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 04 06 05 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 03 06 06 FF 02 02 01 00 01 46 68 7E
15:37:29 Get Next Data block.
15:37:29 Collecting objects
7E A0 14 02 23 21 32 4E 13 E6 E6 00 C0 02 C1 00 00 00 10 59 BF 7E
15:37:30
7E A3 19 21 02 23 52 88 C0 E6 E7 00 C4 02 C1 00 00 00 00 11 00 82 03 00 00 02 04 12 00 04 11 00 09 06 01 00 04 06 06 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 03 06 07 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 04 06 07 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 03 06 08 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 04 06 08 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 09 06 01 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0A 06 01 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 09 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0A 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 09 06 03 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0A 06 03 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 09 06 04 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0A 06 04 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 09 06 05 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0A 06 05 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 09 06 06 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0A 06 06 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 09 06 07 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0A 06 07 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 09 06 08 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0A 06 08 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0E 03 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0E 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0F 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0F 06 01 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0F 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0F 06 03 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 0F 06 04 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 80 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 80 06 01 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 80 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 80 06 03 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 80 06 04 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 81 06 00 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 81 06 01 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 81 06 02 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 70 BF 7E
15:37:30 Get Next Data block.
15:37:30 Collecting objects
7E A0 14 02 23 21 54 7E 15 E6 E6 00 C0 02 C1 00 00 00 11 D0 AE 7E
15:37:31
7E A3 19 21 02 23 74 BC 84 E6 E7 00 C4 02 C1 00 00 00 00 12 00 82 03 00 81 06 03 FF 02 02 01 00 01 00 02 04 12 00 04 11 00 09 06 01 00 81 06 04 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 00 01 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 00 02 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 00 03 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 00 04 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 00 09 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 00 0A 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 00 0F 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 00 80 04 00 FF 02 02 01 00 01 00 02 04 12 00 05 11 00 09 06 01 00 81 04 00 FF 02 02 01 00 01 00 02 04 12 00 06 11 00 09 06 00 00 0E 00 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 01 00 63 0A 01 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 01 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 02 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 03 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 01 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 02 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 03 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 04 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 05 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 06 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 07 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 08 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 09 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 0A 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 0B 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 0C 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 65 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 66 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 67 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 68 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 69 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 6A 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 6B 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 6C 02 02 01 00 01 00 02 04 1A D7 7E
15:37:31 Get Next Data block.
15:37:31 Collecting objects
7E A0 14 02 23 21 76 6E 17 E6 E6 00 C0 02 C1 00 00 00 12 4B 9C 7E
15:37:32
7E A3 19 21 02 23 96 A0 40 E6 E7 00 C4 02 C1 00 00 00 00 13 00 82 03 00 12 00 07 11 01 09 06 00 00 62 01 00 6D 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 6E 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 6F 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 62 01 00 70 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 11 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 0F 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 17 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 13 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 14 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 15 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 16 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 62 00 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 62 01 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 62 02 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 62 04 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 62 05 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 62 06 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 62 07 FF 02 02 01 00 01 00 02 04 12 00 07 11 01 09 06 00 00 63 62 08 FF 02 02 01 00 01 00 02 04 12 00 08 11 00 09 06 00 00 01 00 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 00 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 80 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 81 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 82 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 83 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 84 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 85 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 86 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 87 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 01 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 89 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 8A FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 8B FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 8C FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 8D FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 8E FF 02 02 01 00 01 00 5E 22 7E
15:37:32 Get Next Data block.
15:37:32 Collecting objects
7E A0 14 02 23 21 98 1E 19 E6 E6 00 C0 02 C1 00 00 00 13 C2 8D 7E
15:37:33
7E A3 19 21 02 23 B8 DC 88 E6 E7 00 C4 02 C1 00 00 00 00 14 00 82 03 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 8F FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 90 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 91 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 92 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 93 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 94 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 95 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 96 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 97 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 98 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 99 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 6C FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 9A FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 9B FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 9C FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 9D FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 9E FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 9F FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 A0 FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 6A FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 80 6F FF 02 02 01 00 01 00 02 04 12 00 09 11 00 09 06 00 00 0A 00 A1 FF 02 02 01 00 01 00 02 04 12 00 0B 11 00 09 06 00 00 0B 00 00 FF 02 02 01 00 01 00 02 04 12 00 0F 11 01 09 06 00 00 28 00 00 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 02 03 0F 09 16 01 00 01 02 02 02 0F 01 16 01 02 02 0F 02 16 01 02 04 12 00 0F 11 01 09 06 00 00 28 00 05 FF 02 02 01 09 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 02 03 0F 05 16 01 00 02 03 0F 06 16 01 00 02 03 0F 07 16 01 00 02 03 0F 08 16 01 00 02 03 0F 09 16 01 00 01 00 02 04 12 00 0F 11 01 09 06 00 00 28 00 06 FF 02 02 01 00 01 00 02 04 12 00 11 11 00 09 06 00 00 29 00 00 FF 02 02 01 02 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 01 00 02 04 12 00 12 11 00 09 06 00 00 2C 00 00 FF 02 02 01 00 01 00 02 04 12 00 13 11 01 09 06 00 00 14 00 00 FF 02 02 01 00 01 00 02 04 12 00 14 11 00 93 F5 7E
15:37:33 Get Next Data block.
15:37:33 Collecting objects
7E A0 14 02 23 21 BA 0E 1B E6 E6 00 C0 02 C1 00 00 00 14 7D F9 7E
15:37:34
7E A3 19 21 02 23 DA C8 C8 E6 E7 00 C4 02 C1 00 00 00 00 15 00 82 03 00 09 06 00 01 0D 00 00 FF 02 02 01 00 01 00 02 04 12 00 15 11 00 09 06 00 00 10 01 00 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 01 00 02 04 12 00 15 11 00 09 06 00 00 10 01 01 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 01 00 02 04 12 00 15 11 00 09 06 00 00 10 01 02 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 01 00 02 04 12 00 16 11 00 09 06 00 00 0F 00 04 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 01 00 02 04 12 00 16 11 00 09 06 00 00 0F 00 00 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 01 00 02 04 12 00 16 11 00 09 06 00 00 0F 00 02 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 01 00 02 04 12 00 16 11 00 09 06 00 00 0F 00 05 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 01 00 02 04 12 00 16 11 00 09 06 00 00 0F 00 01 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 01 00 02 04 12 00 16 11 00 09 06 00 00 0F 80 07 FF 02 02 01 04 02 03 0F 01 16 01 00 02 03 0F 02 16 01 00 02 03 0F 03 16 01 00 02 03 0F 04 16 01 00 01 00 02 04 12 00 17 11 01 09 06 00 01 16 00 00 FF 02 02 01 00 01 00 02 04 12 00 17 11 01 09 06 00 02 16 00 00 FF 02 02 01 00 01 00 02 04 12 00 1B 11 01 09 06 00 00 02 00 00 FF 02 02 01 00 01 00 02 04 12 00 1C 11 02 09 06 00 00 02 02 00 FF 02 02 01 00 01 00 02 04 12 00 1D 11 02 09 06 00 00 02 01 00 FF 02 02 01 00 01 00 02 04 12 00 1D 11 02 09 06 00 00 02 02 01 FF 02 02 01 00 01 00 02 04 12 00 28 11 00 09 06 00 00 19 09 00 FF 02 02 01 00 01 00 02 04 12 00 28 11 00 09 06 00 07 19 09 00 FF 02 02 01 00 01 00 02 04 12 00 28 11 00 09 06 00 04 19 09 00 FF 02 02 01 00 01 00 02 04 12 00 28 11 00 09 06 00 08 19 09 00 FF 02 02 01 00 01 00 02 04 12 00 28 11 00 09 06 00 09 19 09 00 FF 02 02 01 00 01 00 02 04 12 00 29 11 00 09 06 00 00 19 00 00 FF 02 02 01 00 01 00 02 04 12 00 2A 11 00 09 06 00 00 19 01 00 FF 02 02 01 00 01 00 02 04 12 00 2D 11 00 09 06 00 00 19 04 00 FF 02 02 01 00 01 00 02 04 12 00 2F 11 00 09 06 00 00 19 06 00 FF 02 02 01 00 E8 D2 7E
15:37:34 Get Next Data block.
15:37:34 Collecting objects
7E A0 14 02 23 21 DC 3E 1D E6 E6 00 C0 02 C1 00 00 00 15 F4 E8 7E
15:37:34
7E A0 E5 21 02 23 FC 17 68 E6 E7 00 C4 02 C1 01 00 00 00 16 00 81 CD 01 00 02 04 12 00 40 11 00 09 06 00 00 2B 00 00 FF 02 02 01 00 01 00 02 04 12 00 40 11 00 09 06 00 00 2B 00 02 FF 02 02 01 00 01 00 02 04 12 00 40 11 00 09 06 00 00 2B 00 03 FF 02 02 01 00 01 00 02 04 12 00 40 11 00 09 06 00 00 2B 00 04 FF 02 02 01 00 01 00 02 04 12 00 40 11 00 09 06 00 00 2B 00 05 FF 02 02 01 00 01 00 02 04 12 00 46 11 00 09 06 00 00 60 03 0A FF 02 02 01 00 01 00 02 04 12 00 6F 11 00 09 06 00 00 13 00 00 FF 02 02 01 00 01 00 02 04 12 00 70 11 00 09 06 00 00 13 0A 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 02 04 12 00 73 11 00 09 06 00 00 13 28 00 FF 02 02 01 01 02 03 0F 01 16 01 00 01 00 75 BB 7E
15:37:35 --- Collecting 606 objects. ---
15:37:35 --- Created 606 objects. ---
15:37:35 --- Reading scalers and units. ---
15:37:35 Reading object 1.0.21.8.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 15 08 00 FF 03 00 F6 23 7E
15:37:35
7E A0 12 21 02 23 1E 71 03 E6 E7 00 C4 01 C1 01 03 73 82 7E
15:37:35 Access Error : Device reports Read-Write denied.
15:37:35 Reading object 1.0.41.8.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 29 08 00 FF 03 00 D2 D5 7E
15:37:35
7E A0 12 21 02 23 30 0D CB E6 E7 00 C4 01 C1 01 03 73 82 7E
15:37:35 Reading object 1.0.61.8.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 3D 08 00 FF 03 00 CE 87 7E
15:37:35
7E A0 12 21 02 23 52 19 8B E6 E7 00 C4 01 C1 01 03 73 82 7E
15:37:35 Reading object 1.0.1.8.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 01 08 00 FF 03 00 EA 71 7E
15:37:36
7E A0 12 21 02 23 74 2D CF E6 E7 00 C4 01 C1 01 03 73 82 7E
15:37:36 Access Error : Device reports Read-Write denied.
15:37:36 Reading object 1.0.1.9.0.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 01 09 00 FF 03 00 AE 7A 7E
15:37:36
7E A0 12 21 02 23 96 31 0B E6 E7 00 C4 01 C1 01 03 73 82 7E
15:37:36 Reading object 1.0.22.8.0.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 16 08 00 FF 03 00 8B 2F 7E
15:37:36
7E A0 12 21 02 23 B8 4D C3 E6 E7 00 C4 01 C1 01 03 73 82 7E
15:37:36 Reading object 1.0.42.8.0.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 2A 08 00 FF 03 00 AF D9 7E
15:37:36
7E A0 12 21 02 23 DA 59 83 E6 E7 00 C4 01 C1 01 03 73 82 7E
15:37:36 Reading object 1.0.62.8.0.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 3E 08 00 FF 03 00 B3 8B 7E
15:37:36
7E A0 12 21 02 23 FC 6D C7 E6 E7 00 C4 01 C1 01 03 73 82 7E
15:37:36 Reading object 1.0.2.8.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 02 08 00 FF 03 00 97 7D 7E
15:37:36
15:37:36 Reading object 1.0.2.9.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 02 09 00 FF 03 00 D3 76 7E
15:37:37
15:37:37 Access Error : Device reports Read-Write denied.
15:37:37 Reading object 1.0.16.8.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 10 08 00 FF 03 00 71 37 7E
15:37:37
15:37:37 Reading object 1.0.23.8.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 17 08 00 FF 03 00 A0 2B 7E
15:37:37
15:37:37 Reading object 1.0.43.8.0.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 2B 08 00 FF 03 00 84 DD 7E
15:37:37
15:37:37 Reading object 1.0.63.8.0.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 3F 08 00 FF 03 00 98 8F 7E
15:37:42 Data send failed. Try to resend 1/2
15:37:42
15:37:42 Access Error : Device reports Read-Write denied.
15:37:42 Reading object 1.0.3.8.0.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 03 08 00 FF 03 00 BC 79 7E
15:37:43
15:37:43 Access Error : Device reports Read-Write denied.
15:37:43 Reading object 1.0.3.9.0.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 03 09 00 FF 03 00 F8 72 7E
15:37:43
15:37:43 Reading object 1.0.24.8.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 18 08 00 FF 03 00 29 16 7E
15:37:43
15:37:43 Reading object 1.0.44.8.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 2C 08 00 FF 03 00 55 C1 7E
15:37:43
15:37:43 Reading object 1.0.64.8.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 40 08 00 FF 03 00 10 77 7E
15:37:43
15:37:43 Reading object 1.0.4.8.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 04 08 00 FF 03 00 6D 65 7E
15:37:48 Data send failed. Try to resend 1/2
15:37:49
15:37:49 Access Error : Device reports Read-Write denied.
15:37:49 Reading object 1.0.4.9.0.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 04 09 00 FF 03 00 29 6E 7E
15:37:49
15:37:49 Reading object 1.0.128.8.0.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 80 08 00 FF 03 00 63 70 7E
15:37:49
15:37:49 Reading object 1.0.25.8.0.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 19 08 00 FF 03 00 02 12 7E
15:37:49
15:37:49 Reading object 1.0.45.8.0.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 2D 08 00 FF 03 00 7E C5 7E
15:37:49
15:37:49 Reading object 1.0.65.8.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 41 08 00 FF 03 00 3B 73 7E
15:37:49
15:37:49 Reading object 1.0.26.8.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 1A 08 00 FF 03 00 7F 1E 7E
15:37:50
15:37:50 Access Error : Device reports Read-Write denied.
15:37:50 Reading object 1.0.46.8.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 2E 08 00 FF 03 00 03 C9 7E
15:37:50
15:37:50 Reading object 1.0.66.8.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 42 08 00 FF 03 00 46 7F 7E
15:37:50
15:37:50 Reading object 1.0.27.8.0.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 1B 08 00 FF 03 00 54 1A 7E
15:37:50
15:37:50 Reading object 1.0.47.8.0.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 2F 08 00 FF 03 00 28 CD 7E
15:37:50
15:37:50 Reading object 1.0.67.8.0.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 43 08 00 FF 03 00 6D 7B 7E
15:37:51
15:37:51 Access Error : Device reports Read-Write denied.
15:37:51 Reading object 1.0.28.8.0.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 1C 08 00 FF 03 00 85 06 7E
15:37:51
15:37:51 Reading object 1.0.48.8.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 30 08 00 FF 03 00 11 B2 7E
15:37:51
15:37:51 Reading object 1.0.68.8.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 44 08 00 FF 03 00 BC 67 7E
15:37:51
15:37:51 Reading object 1.0.29.8.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 1D 08 00 FF 03 00 AE 02 7E
15:37:51
15:37:51 Reading object 1.0.49.8.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 31 08 00 FF 03 00 3A B6 7E
15:37:52
15:37:52 Access Error : Device reports Read-Write denied.
15:37:52 Reading object 1.0.69.8.0.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 45 08 00 FF 03 00 97 63 7E
15:37:52
15:37:52 Reading object 1.0.30.8.0.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 1E 08 00 FF 03 00 D3 0E 7E
15:37:52
15:37:52 Reading object 1.0.50.8.0.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 32 08 00 FF 03 00 47 BA 7E
15:37:52
15:37:52 Reading object 1.0.70.8.0.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 46 08 00 FF 03 00 EA 6F 7E
15:37:52
15:37:52 Reading object 1.0.1.8.1.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 01 08 01 FF 03 00 51 6D 7E
15:37:52
15:37:52 Reading object 1.0.2.8.1.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 02 08 01 FF 03 00 2C 61 7E
15:37:53
15:37:53 Access Error : Device reports Read-Write denied.
15:37:53 Reading object 1.0.1.8.2.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 01 08 02 FF 03 00 9C 48 7E
15:37:53
15:37:53 Reading object 1.0.2.8.2.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 02 08 02 FF 03 00 E1 44 7E
15:37:53
15:37:53 Reading object 1.0.1.8.3.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 01 08 03 FF 03 00 27 54 7E
15:37:53
15:37:53 Reading object 1.0.2.8.3.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 02 08 03 FF 03 00 5A 58 7E
15:37:53
15:37:53 Reading object 1.0.1.8.4.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 01 08 04 FF 03 00 06 03 7E
15:37:54
15:37:54 Access Error : Device reports Read-Write denied.
15:37:54 Reading object 1.0.2.8.4.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 02 08 04 FF 03 00 7B 0F 7E
15:37:54
15:37:54 Reading object 1.0.1.8.5.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 01 08 05 FF 03 00 BD 1F 7E
15:37:54
15:37:54 Reading object 1.0.2.8.5.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 02 08 05 FF 03 00 C0 13 7E
15:37:59 Data send failed. Try to resend 1/2
15:37:59
15:37:59 Access Error : Device reports Read-Write denied.
15:37:59 Reading object 1.0.1.8.6.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 01 08 06 FF 03 00 70 3A 7E
15:37:59
15:37:59 Reading object 1.0.2.8.6.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 02 08 06 FF 03 00 0D 36 7E
15:38:00
15:38:00 Access Error : Device reports Read-Write denied.
15:38:00 Reading object 1.0.1.8.7.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 01 08 07 FF 03 00 CB 26 7E
15:38:00
15:38:00 Reading object 1.0.2.8.7.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 02 08 07 FF 03 00 B6 2A 7E
15:38:00
15:38:00 Reading object 1.0.1.8.8.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 01 08 08 FF 03 00 32 94 7E
15:38:00
15:38:00 Reading object 1.0.2.8.8.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 02 08 08 FF 03 00 4F 98 7E
15:38:00
15:38:00 Reading object 1.0.1.8.9.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 01 08 09 FF 03 00 89 88 7E
15:38:01
15:38:01 Access Error : Device reports Read-Write denied.
15:38:01 Reading object 1.0.2.8.9.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 02 08 09 FF 03 00 F4 84 7E
15:38:01
15:38:01 Reading object 1.0.1.8.10.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 01 08 0A FF 03 00 44 AD 7E
15:38:06 Data send failed. Try to resend 1/2
15:38:06
15:38:06 Access Error : Device reports Read-Write denied.
15:38:06 Reading object 1.0.2.8.10.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 02 08 0A FF 03 00 39 A1 7E
15:38:06
15:38:06 Reading object 1.0.1.8.11.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 01 08 0B FF 03 00 FF B1 7E
15:38:06
15:38:06 Reading object 1.0.2.8.11.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 02 08 0B FF 03 00 82 BD 7E
15:38:07
15:38:07 Access Error : Device reports Read-Write denied.
15:38:07 Reading object 1.0.1.8.12.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 01 08 0C FF 03 00 DE E6 7E
15:38:07
15:38:07 Reading object 1.0.2.8.12.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 02 08 0C FF 03 00 A3 EA 7E
15:38:07
15:38:07 Reading object 1.0.1.8.13.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 01 08 0D FF 03 00 65 FA 7E
15:38:07
15:38:07 Reading object 1.0.2.8.13.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 02 08 0D FF 03 00 18 F6 7E
15:38:07
15:38:07 Reading object 1.0.1.8.14.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 01 08 0E FF 03 00 A8 DF 7E
15:38:07
15:38:07 Reading object 1.0.2.8.14.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 02 08 0E FF 03 00 D5 D3 7E
15:38:12 Data send failed. Try to resend 1/2
15:38:13
15:38:13 Access Error : Device reports Read-Write denied.
15:38:13 Reading object 1.0.1.8.15.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 01 08 0F FF 03 00 13 C3 7E
15:38:13
15:38:13 Reading object 1.0.2.8.15.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 02 08 0F FF 03 00 6E CF 7E
15:38:13
15:38:13 Reading object 1.0.1.8.16.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 01 08 10 FF 03 00 4B B2 7E
15:38:13
15:38:13 Reading object 1.0.2.8.16.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 02 08 10 FF 03 00 36 BE 7E
15:38:13
15:38:13 Reading object 1.0.1.8.17.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 01 08 11 FF 03 00 F0 AE 7E
15:38:14
15:38:14 Access Error : Device reports Read-Write denied.
15:38:14 Reading object 1.0.2.8.17.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 02 08 11 FF 03 00 8D A2 7E
15:38:14
15:38:14 Reading object 1.0.1.8.18.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 01 08 12 FF 03 00 3D 8B 7E
15:38:19 Data send failed. Try to resend 1/2
15:38:19
15:38:19 Access Error : Device reports Read-Write denied.
15:38:19 Reading object 1.0.2.8.18.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 02 08 12 FF 03 00 40 87 7E
15:38:19
15:38:19 Reading object 1.0.1.8.19.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 01 08 13 FF 03 00 86 97 7E
15:38:19
15:38:19 Reading object 1.0.2.8.19.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 02 08 13 FF 03 00 FB 9B 7E
15:38:20
15:38:20 Access Error : Device reports Read-Write denied.
15:38:20 Reading object 1.0.1.8.20.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 01 08 14 FF 03 00 A7 C0 7E
15:38:20
15:38:20 Reading object 1.0.2.8.20.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 02 08 14 FF 03 00 DA CC 7E
15:38:20
15:38:20 Reading object 1.0.1.8.21.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 01 08 15 FF 03 00 1C DC 7E
15:38:20
15:38:20 Reading object 1.0.2.8.21.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 02 08 15 FF 03 00 61 D0 7E
15:38:20
15:38:20 Reading object 1.0.1.8.22.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 01 08 16 FF 03 00 D1 F9 7E
15:38:21
15:38:21 Access Error : Device reports Read-Write denied.
15:38:21 Reading object 1.0.2.8.22.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 02 08 16 FF 03 00 AC F5 7E
15:38:26 Data send failed. Try to resend 1/2
15:38:26
15:38:26 Access Error : Device reports Read-Write denied.
15:38:26 Reading object 1.0.1.8.23.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 01 08 17 FF 03 00 6A E5 7E
15:38:26
15:38:26 Reading object 1.0.2.8.23.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 02 08 17 FF 03 00 17 E9 7E
15:38:26
15:38:26 Reading object 1.0.1.8.24.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 01 08 18 FF 03 00 93 57 7E
15:38:26
15:38:26 Reading object 1.0.2.8.24.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 02 08 18 FF 03 00 EE 5B 7E
15:38:26
15:38:26 Reading object 1.0.3.8.1.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 03 08 01 FF 03 00 07 65 7E
15:38:27
15:38:27 Access Error : Device reports Read-Write denied.
15:38:27 Reading object 1.0.4.8.1.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 04 08 01 FF 03 00 D6 79 7E
15:38:27
15:38:27 Reading object 1.0.3.8.2.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 03 08 02 FF 03 00 CA 40 7E
15:38:27
15:38:27 Reading object 1.0.4.8.2.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 04 08 02 FF 03 00 1B 5C 7E
15:38:27
15:38:27 Reading object 1.0.3.8.3.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 03 08 03 FF 03 00 71 5C 7E
15:38:27
15:38:27 Reading object 1.0.4.8.3.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 04 08 03 FF 03 00 A0 40 7E
15:38:28
15:38:28 Access Error : Device reports Read-Write denied.
15:38:28 Reading object 1.0.3.8.4.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 03 08 04 FF 03 00 50 0B 7E
15:38:28
15:38:28 Reading object 1.0.4.8.4.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 04 08 04 FF 03 00 81 17 7E
15:38:28
15:38:28 Reading object 1.0.3.8.5.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 03 08 05 FF 03 00 EB 17 7E
15:38:28
15:38:28 Reading object 1.0.4.8.5.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 04 08 05 FF 03 00 3A 0B 7E
15:38:33 Data send failed. Try to resend 1/2
15:38:33
15:38:33 Access Error : Device reports Read-Write denied.
15:38:33 Reading object 1.0.3.8.6.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 03 08 06 FF 03 00 26 32 7E
15:38:34
15:38:34 Access Error : Device reports Read-Write denied.
15:38:34 Reading object 1.0.4.8.6.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 04 08 06 FF 03 00 F7 2E 7E
15:38:34
15:38:34 Reading object 1.0.3.8.7.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 03 08 07 FF 03 00 9D 2E 7E
15:38:34
15:38:34 Reading object 1.0.4.8.7.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 04 08 07 FF 03 00 4C 32 7E
15:38:34
15:38:34 Reading object 1.0.3.8.8.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 03 08 08 FF 03 00 64 9C 7E
15:38:34
15:38:34 Reading object 1.0.4.8.8.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 04 08 08 FF 03 00 B5 80 7E
15:38:34
15:38:34 Reading object 1.0.3.8.9.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 03 08 09 FF 03 00 DF 80 7E
15:38:39 Data send failed. Try to resend 1/2
15:38:40
15:38:40 Access Error : Device reports Read-Write denied.
15:38:40 Reading object 1.0.4.8.9.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 04 08 09 FF 03 00 0E 9C 7E
15:38:40
15:38:40 Reading object 1.0.3.8.10.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 03 08 0A FF 03 00 12 A5 7E
15:38:40
15:38:40 Reading object 1.0.4.8.10.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 04 08 0A FF 03 00 C3 B9 7E
15:38:40
15:38:40 Reading object 1.0.3.8.11.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 03 08 0B FF 03 00 A9 B9 7E
15:38:40
15:38:40 Reading object 1.0.4.8.11.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 04 08 0B FF 03 00 78 A5 7E
15:38:41
15:38:41 Access Error : Device reports Read-Write denied.
15:38:41 Reading object 1.0.3.8.12.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 03 08 0C FF 03 00 88 EE 7E
15:38:41
15:38:41 Reading object 1.0.4.8.12.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 04 08 0C FF 03 00 59 F2 7E
15:38:41
15:38:41 Reading object 1.0.3.8.13.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 03 08 0D FF 03 00 33 F2 7E
15:38:46 Data send failed. Try to resend 1/2
15:38:46
15:38:46 Access Error : Device reports Read-Write denied.
15:38:46 Reading object 1.0.4.8.13.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 04 08 0D FF 03 00 E2 EE 7E
15:38:46
15:38:46 Reading object 1.0.3.8.14.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 03 08 0E FF 03 00 FE D7 7E
15:38:47
15:38:47 Access Error : Device reports Read-Write denied.
15:38:47 Reading object 1.0.4.8.14.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 04 08 0E FF 03 00 2F CB 7E
15:38:47
15:38:47 Reading object 1.0.3.8.15.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 03 08 0F FF 03 00 45 CB 7E
15:38:47
15:38:47 Reading object 1.0.4.8.15.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 04 08 0F FF 03 00 94 D7 7E
15:38:47
15:38:47 Reading object 1.0.3.8.16.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 03 08 10 FF 03 00 1D BA 7E
15:38:47
15:38:47 Reading object 1.0.4.8.16.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 04 08 10 FF 03 00 CC A6 7E
15:38:47
15:38:47 Reading object 1.0.3.8.17.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 03 08 11 FF 03 00 A6 A6 7E
15:38:48
15:38:48 Access Error : Device reports Read-Write denied.
15:38:48 Reading object 1.0.4.8.17.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 04 08 11 FF 03 00 77 BA 7E
15:38:48
15:38:48 Reading object 1.0.3.8.18.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 03 08 12 FF 03 00 6B 83 7E
15:38:48
15:38:48 Reading object 1.0.4.8.18.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 04 08 12 FF 03 00 BA 9F 7E
15:38:48
15:38:48 Reading object 1.0.3.8.19.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 03 08 13 FF 03 00 D0 9F 7E
15:38:48
15:38:48 Reading object 1.0.4.8.19.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 04 08 13 FF 03 00 01 83 7E
15:38:49
15:38:49 Access Error : Device reports Read-Write denied.
15:38:49 Reading object 1.0.3.8.20.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 03 08 14 FF 03 00 F1 C8 7E
15:38:49
15:38:49 Reading object 1.0.4.8.20.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 04 08 14 FF 03 00 20 D4 7E
15:38:54 Data send failed. Try to resend 1/2
15:38:54
15:38:54 Access Error : Device reports Read-Write denied.
15:38:54 Reading object 1.0.3.8.21.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 03 08 15 FF 03 00 4A D4 7E
15:38:54
15:38:54 Reading object 1.0.4.8.21.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 04 08 15 FF 03 00 9B C8 7E
15:38:54
15:38:54 Reading object 1.0.3.8.22.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 03 08 16 FF 03 00 87 F1 7E
15:38:55
15:38:55 Access Error : Device reports Read-Write denied.
15:38:55 Reading object 1.0.4.8.22.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 04 08 16 FF 03 00 56 ED 7E
15:38:55
15:38:55 Reading object 1.0.3.8.23.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 03 08 17 FF 03 00 3C ED 7E
15:38:55
15:38:55 Reading object 1.0.4.8.23.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 04 08 17 FF 03 00 ED F1 7E
15:38:55
15:38:55 Reading object 1.0.3.8.24.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 03 08 18 FF 03 00 C5 5F 7E
15:38:55
15:38:55 Reading object 1.0.4.8.24.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 04 08 18 FF 03 00 14 43 7E
15:38:56
15:38:56 Access Error : Device reports Read-Write denied.
15:38:56 Reading object 1.0.9.8.1.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 09 08 01 FF 03 00 09 4C 7E
15:39:01 Data send failed. Try to resend 1/2
15:39:01
15:39:01 Access Error : Device reports Read-Write denied.
15:39:01 Reading object 1.0.10.8.1.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 01 FF 03 00 74 40 7E
15:39:01
15:39:01 Reading object 1.0.9.8.2.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 09 08 02 FF 03 00 C4 69 7E
15:39:01
15:39:01 Reading object 1.0.10.8.2.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 02 FF 03 00 B9 65 7E
15:39:01
15:39:01 Reading object 1.0.9.8.3.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 09 08 03 FF 03 00 7F 75 7E
15:39:01
15:39:01 Reading object 1.0.10.8.3.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 03 FF 03 00 02 79 7E
15:39:02
15:39:02 Access Error : Device reports Read-Write denied.
15:39:02 Reading object 1.0.9.8.4.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 09 08 04 FF 03 00 5E 22 7E
15:39:07 Data send failed. Try to resend 1/2
15:39:07
15:39:07 Access Error : Device reports Read-Write denied.
15:39:07 Reading object 1.0.10.8.4.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 0A 08 04 FF 03 00 23 2E 7E
15:39:07
15:39:07 Reading object 1.0.9.8.5.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 09 08 05 FF 03 00 E5 3E 7E
15:39:07
15:39:07 Reading object 1.0.10.8.5.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 05 FF 03 00 98 32 7E
15:39:07
15:39:07 Reading object 1.0.9.8.6.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 09 08 06 FF 03 00 28 1B 7E
15:39:08
15:39:08 Access Error : Device reports Read-Write denied.
15:39:08 Reading object 1.0.10.8.6.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 06 FF 03 00 55 17 7E
15:39:08
15:39:08 Reading object 1.0.9.8.7.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 09 08 07 FF 03 00 93 07 7E
15:39:08
15:39:08 Reading object 1.0.10.8.7.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 07 FF 03 00 EE 0B 7E
15:39:08
15:39:08 Reading object 1.0.9.8.8.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 09 08 08 FF 03 00 6A B5 7E
15:39:08
15:39:08 Reading object 1.0.10.8.8.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 0A 08 08 FF 03 00 17 B9 7E
15:39:09
15:39:09 Access Error : Device reports Read-Write denied.
15:39:09 Reading object 1.0.9.8.9.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 09 08 09 FF 03 00 D1 A9 7E
15:39:09
15:39:09 Reading object 1.0.10.8.9.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 09 FF 03 00 AC A5 7E
15:39:09
15:39:09 Reading object 1.0.9.8.10.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 09 08 0A FF 03 00 1C 8C 7E
15:39:09
15:39:09 Reading object 1.0.10.8.10.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 0A FF 03 00 61 80 7E
15:39:09
15:39:09 Reading object 1.0.9.8.11.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 09 08 0B FF 03 00 A7 90 7E
15:39:09
15:39:09 Reading object 1.0.10.8.11.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 0B FF 03 00 DA 9C 7E
15:39:10
15:39:10 Access Error : Device reports Read-Write denied.
15:39:10 Reading object 1.0.9.8.12.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 09 08 0C FF 03 00 86 C7 7E
15:39:10
15:39:10 Reading object 1.0.10.8.12.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 0A 08 0C FF 03 00 FB CB 7E
15:39:10
15:39:10 Reading object 1.0.9.8.13.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 09 08 0D FF 03 00 3D DB 7E
15:39:10
15:39:10 Reading object 1.0.10.8.13.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 0D FF 03 00 40 D7 7E
15:39:10
15:39:10 Reading object 1.0.9.8.14.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 09 08 0E FF 03 00 F0 FE 7E
15:39:15 Data send failed. Try to resend 1/2
15:39:16
15:39:16 Access Error : Device reports Read-Write denied.
15:39:16 Reading object 1.0.10.8.14.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 0E FF 03 00 8D F2 7E
15:39:16
15:39:16 Reading object 1.0.9.8.15.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 09 08 0F FF 03 00 4B E2 7E
15:39:16
15:39:16 Reading object 1.0.10.8.15.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 0F FF 03 00 36 EE 7E
15:39:16
15:39:16 Reading object 1.0.9.8.16.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 09 08 10 FF 03 00 13 93 7E
15:39:16
15:39:16 Reading object 1.0.10.8.16.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 0A 08 10 FF 03 00 6E 9F 7E
15:39:17
15:39:17 Access Error : Device reports Read-Write denied.
15:39:17 Reading object 1.0.9.8.17.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 09 08 11 FF 03 00 A8 8F 7E
15:39:17
15:39:17 Reading object 1.0.10.8.17.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 11 FF 03 00 D5 83 7E
15:39:22 Data send failed. Try to resend 1/2
15:39:22
15:39:22 Access Error : Device reports Read-Write denied.
15:39:22 Reading object 1.0.9.8.18.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 09 08 12 FF 03 00 65 AA 7E
15:39:22
15:39:22 Reading object 1.0.10.8.18.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 12 FF 03 00 18 A6 7E
15:39:22
15:39:22 Reading object 1.0.9.8.19.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 09 08 13 FF 03 00 DE B6 7E
15:39:22
15:39:22 Reading object 1.0.10.8.19.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 13 FF 03 00 A3 BA 7E
15:39:23
15:39:23 Access Error : Device reports Read-Write denied.
15:39:23 Reading object 1.0.9.8.20.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 09 08 14 FF 03 00 FF E1 7E
15:39:23
15:39:23 Reading object 1.0.10.8.20.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 0A 08 14 FF 03 00 82 ED 7E
15:39:23
15:39:23 Reading object 1.0.9.8.21.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 09 08 15 FF 03 00 44 FD 7E
15:39:23
15:39:23 Reading object 1.0.10.8.21.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 15 FF 03 00 39 F1 7E
15:39:28 Data send failed. Try to resend 1/2
15:39:28
15:39:28 Access Error : Device reports Read-Write denied.
15:39:28 Reading object 1.0.9.8.22.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 09 08 16 FF 03 00 89 D8 7E
15:39:29
15:39:29 Access Error : Device reports Read-Write denied.
15:39:29 Reading object 1.0.10.8.22.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 16 FF 03 00 F4 D4 7E
15:39:29
15:39:29 Reading object 1.0.9.8.23.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 09 08 17 FF 03 00 32 C4 7E
15:39:29
15:39:29 Reading object 1.0.10.8.23.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 17 FF 03 00 4F C8 7E
15:39:29
15:39:29 Reading object 1.0.9.8.24.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 09 08 18 FF 03 00 CB 76 7E
15:39:29
15:39:29 Reading object 1.0.10.8.24.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 0A 08 18 FF 03 00 B6 7A 7E
15:39:30
15:39:30 Access Error : Device reports Read-Write denied.
15:39:30 Reading object 1.0.21.7.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 15 07 00 FF 03 00 0A 49 7E
15:39:35 Data send failed. Try to resend 1/2
15:39:35
15:39:35 Access Error : Device reports Read-Write denied.
15:39:35 Reading object 1.0.41.7.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 29 07 00 FF 03 00 2E BF 7E
15:39:35
15:39:35 Reading object 1.0.61.7.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 3D 07 00 FF 03 00 32 ED 7E
15:39:35
15:39:35 Reading object 1.0.22.7.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 16 07 00 FF 03 00 77 45 7E
15:39:35
15:39:35 Reading object 1.0.42.7.0.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 2A 07 00 FF 03 00 53 B3 7E
15:39:35
15:39:35 Reading object 1.0.62.7.0.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 3E 07 00 FF 03 00 4F E1 7E
15:39:36
15:39:36 Access Error : Device reports Read-Write denied.
15:39:36 Reading object 1.0.1.7.0.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 01 07 00 FF 03 00 16 1B 7E
15:39:36
15:39:36 Reading object 1.0.2.7.0.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 02 07 00 FF 03 00 6B 17 7E
15:39:36
15:39:36 Reading object 1.0.23.7.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 17 07 00 FF 03 00 5C 41 7E
15:39:36
15:39:36 Reading object 1.0.43.7.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 2B 07 00 FF 03 00 78 B7 7E
15:39:36
15:39:36 Reading object 1.0.63.7.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 3F 07 00 FF 03 00 64 E5 7E
15:39:37
15:39:37 Access Error : Device reports Read-Write denied.
15:39:37 Reading object 1.0.24.7.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 18 07 00 FF 03 00 D5 7C 7E
15:39:37
15:39:37 Reading object 1.0.44.7.0.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 2C 07 00 FF 03 00 A9 AB 7E
15:39:37
15:39:37 Reading object 1.0.64.7.0.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 40 07 00 FF 03 00 EC 1D 7E
15:39:37
15:39:37 Reading object 1.0.3.7.0.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 03 07 00 FF 03 00 40 13 7E
15:39:37
15:39:37 Reading object 1.0.4.7.0.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 04 07 00 FF 03 00 91 0F 7E
15:39:38
15:39:38 Access Error : Device reports Read-Write denied.
15:39:38 Reading object 1.0.29.7.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 1D 07 00 FF 03 00 52 68 7E
15:39:38
15:39:38 Reading object 1.0.49.7.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 31 07 00 FF 03 00 C6 DC 7E
15:39:38
15:39:38 Reading object 1.0.69.7.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 45 07 00 FF 03 00 6B 09 7E
15:39:38
15:39:38 Reading object 1.0.30.7.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 1E 07 00 FF 03 00 2F 64 7E
15:39:38
15:39:38 Reading object 1.0.50.7.0.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 32 07 00 FF 03 00 BB D0 7E
15:39:38
15:39:38 Reading object 1.0.70.7.0.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 46 07 00 FF 03 00 16 05 7E
15:39:39
15:39:39 Access Error : Device reports Read-Write denied.
15:39:39 Reading object 1.0.9.7.0.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 09 07 00 FF 03 00 4E 3A 7E
15:39:39
15:39:39 Reading object 1.0.10.7.0.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 0A 07 00 FF 03 00 33 36 7E
15:39:39
15:39:39 Reading object 1.0.33.7.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 21 07 00 FF 03 00 76 9E 7E
15:39:39
15:39:39 Reading object 1.0.53.7.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 35 07 00 FF 03 00 6A CC 7E
15:39:39
15:39:39 Reading object 1.0.73.7.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 49 07 00 FF 03 00 9F 38 7E
15:39:40
15:39:40 Access Error : Device reports Read-Write denied.
15:39:40 Reading object 1.0.13.7.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 0D 07 00 FF 03 00 E2 2A 7E
15:39:40
15:39:40 Reading object 1.0.32.7.0.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 20 07 00 FF 03 00 5D 9A 7E
15:39:40
15:39:40 Reading object 1.0.52.7.0.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 34 07 00 FF 03 00 41 C8 7E
15:39:40
15:39:40 Reading object 1.0.72.7.0.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 48 07 00 FF 03 00 B4 3C 7E
15:39:40
15:39:40 Reading object 1.0.92.7.0.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 5C 07 00 FF 03 00 A8 6E 7E
15:39:41
15:39:41 Access Error : Device reports Read-Write denied.
15:39:41 Reading object 1.0.31.7.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 1F 07 00 FF 03 00 04 60 7E
15:39:41
15:39:41 Reading object 1.0.51.7.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 33 07 00 FF 03 00 90 D4 7E
15:39:41
15:39:41 Reading object 1.0.71.7.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 47 07 00 FF 03 00 3D 01 7E
15:39:41
15:39:41 Reading object 1.0.91.7.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 5B 07 00 FF 03 00 79 72 7E
15:39:41
15:39:41 Reading object 0.0.96.6.3.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 00 00 60 06 03 FF 03 00 BA 37 7E
15:39:42
15:39:42 Access Error : Device reports Read-Write denied.
15:39:42 Reading object 0.0.96.6.11.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 00 00 60 06 0B FF 03 00 62 D2 7E
15:39:42
15:39:42 Reading object 1.0.14.7.0.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 0E 07 00 FF 03 00 9F 26 7E
15:39:42
15:39:42 Reading object 1.0.12.31.0.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 0C 1F 00 FF 03 00 A9 C0 7E
15:39:42
15:39:42 Reading object 1.0.12.33.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 0C 21 00 FF 03 00 C0 75 7E
15:39:42
15:39:42 Reading object 1.0.12.35.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 0C 23 00 FF 03 00 48 63 7E
15:39:43
15:39:43 Access Error : Device reports Read-Write denied.
15:39:43 Reading object 1.0.12.37.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 0C 25 00 FF 03 00 D0 58 7E
15:39:43
15:39:43 Reading object 1.0.32.7.124.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 20 07 7C FF 03 00 2C 57 7E
15:39:43
15:39:43 Reading object 1.0.52.7.124.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 34 07 7C FF 03 00 30 05 7E
15:39:43
15:39:43 Reading object 1.0.72.7.124.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 48 07 7C FF 03 00 C5 F1 7E
15:39:43
15:39:43 Reading object 1.0.12.7.124.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 0C 07 7C FF 03 00 B8 E3 7E
15:39:43
15:39:43 Reading object 1.0.31.7.124.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 1F 07 7C FF 03 00 75 AD 7E
15:39:44
15:39:44 Access Error : Device reports Read-Write denied.
15:39:44 Reading object 1.0.51.7.124.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 33 07 7C FF 03 00 E1 19 7E
15:39:44
15:39:44 Reading object 1.0.71.7.124.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 47 07 7C FF 03 00 4C CC 7E
15:39:44
15:39:44 Reading object 1.0.11.7.124.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 0B 07 7C FF 03 00 69 FF 7E
15:39:44
15:39:44 Reading object 1.0.31.7.125.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 1F 07 7D FF 03 00 CE B1 7E
15:39:44
15:39:44 Reading object 1.0.51.7.125.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 33 07 7D FF 03 00 5A 05 7E
15:39:45
15:39:45 Access Error : Device reports Read-Write denied.
15:39:45 Reading object 1.0.71.7.125.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 47 07 7D FF 03 00 F7 D0 7E
15:39:45
15:39:45 Reading object 1.0.11.7.125.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 0B 07 7D FF 03 00 D2 E3 7E
15:39:45
15:39:45 Reading object 0.0.96.8.0.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 00 00 60 08 00 FF 03 00 CF 73 7E
15:39:45
15:39:45 Reading object 1.0.9.8.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 09 08 00 FF 03 00 B2 50 7E
15:39:45
15:39:45 Reading object 1.0.10.8.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 0A 08 00 FF 03 00 CF 5C 7E
15:39:46
15:39:46 Access Error : Device reports Read-Write denied.
15:39:46 Reading object 1.0.34.7.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 22 07 00 FF 03 00 0B 92 7E
15:39:46
15:39:46 Reading object 1.0.54.7.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 36 07 00 FF 03 00 17 C0 7E
15:39:46
15:39:46 Reading object 1.0.74.7.0.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 4A 07 00 FF 03 00 E2 34 7E
15:39:46
15:39:46 Reading object 1.0.81.7.40.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 51 07 28 FF 03 00 FC 31 7E
15:39:46
15:39:46 Reading object 1.0.81.7.51.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 51 07 33 FF 03 00 48 32 7E
15:39:46
15:39:46 Reading object 1.0.81.7.62.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 51 07 3E FF 03 00 C7 B9 7E
15:39:47
15:39:47 Access Error : Device reports Read-Write denied.
15:39:47 Reading object 1.0.81.7.1.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 51 07 01 FF 03 00 CC 47 7E
15:39:47
15:39:47 Reading object 1.0.81.7.2.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 51 07 02 FF 03 00 01 62 7E
15:39:47
15:39:47 Reading object 1.0.81.7.21.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 51 07 15 FF 03 00 81 F6 7E
15:39:47
15:39:47 Reading object 1.0.81.7.45.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 51 07 2D FF 03 00 AB 5F 7E
15:39:47
15:39:47 Reading object 1.0.81.7.46.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 51 07 2E FF 03 00 66 7A 7E
15:39:48
15:39:48 Access Error : Device reports Read-Write denied.
15:39:48 Reading object 1.0.81.7.56.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 51 07 38 FF 03 00 5D F2 7E
15:39:53 Data send failed. Try to resend 1/2
15:39:53
15:39:53 Access Error : Device reports Read-Write denied.
15:39:53 Reading object 1.0.5.7.0.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 01 00 05 07 00 FF 03 00 BA 0B 7E
15:39:53
15:39:53 Reading object 1.0.6.7.0.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 01 00 06 07 00 FF 03 00 C7 07 7E
15:39:53
15:39:53 Reading object 1.0.7.7.0.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 01 00 07 07 00 FF 03 00 EC 03 7E
15:39:53
15:39:53 Reading object 1.0.8.7.0.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 08 07 00 FF 03 00 65 3E 7E
15:39:53
15:39:53 Reading object 0.0.96.9.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 00 00 60 09 00 FF 03 00 8B 78 7E
15:39:54
15:39:54 Access Error : Device reports Read-Write denied.
15:39:54 Reading object 1.0.15.8.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 0F 08 00 FF 03 00 48 48 7E
15:39:54
15:39:54 Reading object 1.0.16.8.0.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 10 08 00 FF 03 00 71 37 7E
15:39:54
15:39:54 Reading object 0.0.131.0.15.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 00 00 83 00 0F FF 03 00 78 15 7E
15:39:59 Data send failed. Try to resend 1/2
15:39:59
15:39:59 Access Error : Device reports Read-Write denied.
15:39:59 Reading object 0.0.131.0.16.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 00 00 83 00 10 FF 03 00 20 64 7E
15:39:59
15:39:59 Reading object 0.0.131.0.17.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 00 00 83 00 11 FF 03 00 9B 78 7E
15:40:00
15:40:00 Access Error : Device reports Read-Write denied.
15:40:00 Reading object 0.0.131.0.18.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 00 00 83 00 12 FF 03 00 56 5D 7E
15:40:00
15:40:00 Reading object 0.0.131.0.19.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 00 00 83 00 13 FF 03 00 ED 41 7E
15:40:00
15:40:00 Reading object 1.0.15.35.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 0F 23 00 FF 03 00 35 6F 7E
15:40:00
15:40:00 Reading object 1.0.11.35.0.255, interface Register
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 03 01 00 0B 23 00 FF 03 00 99 7F 7E
15:40:00
15:40:00 Reading object 1.0.90.7.0.255, interface Register
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 03 01 00 5A 07 00 FF 03 00 52 76 7E
15:40:05 Data send failed. Try to resend 1/2
15:40:06
15:40:06 Access Error : Device reports Read-Write denied.
15:40:06 Reading object 1.0.15.7.0.255, interface Register
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 03 01 00 0F 07 00 FF 03 00 B4 22 7E
15:40:06
15:40:06 Reading object 0.0.131.0.20.255, interface Register
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 03 00 00 83 00 14 FF 03 00 CC 16 7E
15:40:06
15:40:06 Reading object 0.0.131.0.21.255, interface Register
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 03 00 00 83 00 15 FF 03 00 77 0A 7E
15:40:06
15:40:06 Reading object 0.0.131.0.43.255, interface Register
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 03 00 00 83 00 2B FF 03 00 C7 E8 7E
15:40:06
15:40:06 Reading object 1.0.0.9.11.255, interface Register
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 03 01 00 00 09 0B FF 03 00 90 BE 7E
15:40:07
15:40:07 Access Error : Device reports Read-Write denied.
15:40:07 Reading object 1.0.0.3.0.255, interface Register
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 03 01 00 00 03 00 FF 03 00 2D 32 7E
15:40:07
15:40:07 Reading object 1.0.1.6.0.255, interface ExtendedRegister
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 04 01 00 01 06 00 FF 03 00 B0 F9 7E
15:40:07
15:40:07 Reading object 1.0.2.6.0.255, interface ExtendedRegister
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 04 01 00 02 06 00 FF 03 00 CD F5 7E
15:40:12 Data send failed. Try to resend 1/2
15:40:12
15:40:12 Access Error : Device reports Read-Write denied.
15:40:12 Reading object 1.0.3.6.0.255, interface ExtendedRegister
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 04 01 00 03 06 00 FF 03 00 E6 F1 7E
15:40:12
15:40:12 Reading object 1.0.4.6.0.255, interface ExtendedRegister
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 04 01 00 04 06 00 FF 03 00 37 ED 7E
15:40:13
15:40:13 Access Error : Device reports Read-Write denied.
15:40:13 Reading object 1.0.9.6.0.255, interface ExtendedRegister
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 04 01 00 09 06 00 FF 03 00 E8 D8 7E
15:40:13
15:40:13 Reading object 1.0.10.6.0.255, interface ExtendedRegister
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 04 01 00 0A 06 00 FF 03 00 95 D4 7E
15:40:13
15:40:13 Reading object 1.0.1.6.1.255, interface ExtendedRegister
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 04 01 00 01 06 01 FF 03 00 0B E5 7E
15:40:13
15:40:13 Reading object 1.0.2.6.1.255, interface ExtendedRegister
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 04 01 00 02 06 01 FF 03 00 76 E9 7E
15:40:13
15:40:13 Reading object 1.0.1.6.2.255, interface ExtendedRegister
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 04 01 00 01 06 02 FF 03 00 C6 C0 7E
15:40:13
15:40:13 Reading object 1.0.2.6.2.255, interface ExtendedRegister
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 04 01 00 02 06 02 FF 03 00 BB CC 7E
15:40:14
15:40:14 Access Error : Device reports Read-Write denied.
15:40:14 Reading object 1.0.1.6.3.255, interface ExtendedRegister
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 04 01 00 01 06 03 FF 03 00 7D DC 7E
15:40:14
15:40:14 Reading object 1.0.2.6.3.255, interface ExtendedRegister
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 04 01 00 02 06 03 FF 03 00 00 D0 7E
15:40:14
15:40:14 Reading object 1.0.1.6.4.255, interface ExtendedRegister
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 04 01 00 01 06 04 FF 03 00 5C 8B 7E
15:40:14
15:40:14 Reading object 1.0.2.6.4.255, interface ExtendedRegister
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 04 01 00 02 06 04 FF 03 00 21 87 7E
15:40:14
15:40:14 Reading object 1.0.1.6.5.255, interface ExtendedRegister
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 04 01 00 01 06 05 FF 03 00 E7 97 7E
15:40:15
15:40:15 Access Error : Device reports Read-Write denied.
15:40:15 Reading object 1.0.2.6.5.255, interface ExtendedRegister
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 04 01 00 02 06 05 FF 03 00 9A 9B 7E
15:40:15
15:40:15 Reading object 1.0.1.6.6.255, interface ExtendedRegister
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 04 01 00 01 06 06 FF 03 00 2A B2 7E
15:40:15
15:40:15 Reading object 1.0.2.6.6.255, interface ExtendedRegister
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 04 01 00 02 06 06 FF 03 00 57 BE 7E
15:40:15
15:40:15 Reading object 1.0.1.6.7.255, interface ExtendedRegister
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 04 01 00 01 06 07 FF 03 00 91 AE 7E
15:40:15
15:40:15 Reading object 1.0.2.6.7.255, interface ExtendedRegister
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 04 01 00 02 06 07 FF 03 00 EC A2 7E
15:40:16
15:40:16 Access Error : Device reports Read-Write denied.
15:40:16 Reading object 1.0.1.6.8.255, interface ExtendedRegister
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 04 01 00 01 06 08 FF 03 00 68 1C 7E
15:40:16
15:40:16 Reading object 1.0.2.6.8.255, interface ExtendedRegister
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 04 01 00 02 06 08 FF 03 00 15 10 7E
15:40:16
15:40:16 Reading object 1.0.3.6.1.255, interface ExtendedRegister
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 04 01 00 03 06 01 FF 03 00 5D ED 7E
15:40:16
15:40:16 Reading object 1.0.4.6.1.255, interface ExtendedRegister
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 04 01 00 04 06 01 FF 03 00 8C F1 7E
15:40:16
15:40:16 Reading object 1.0.3.6.2.255, interface ExtendedRegister
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 04 01 00 03 06 02 FF 03 00 90 C8 7E
15:40:17
15:40:17 Access Error : Device reports Read-Write denied.
15:40:17 Reading object 1.0.4.6.2.255, interface ExtendedRegister
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 04 01 00 04 06 02 FF 03 00 41 D4 7E
15:40:17
15:40:17 Reading object 1.0.3.6.3.255, interface ExtendedRegister
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 04 01 00 03 06 03 FF 03 00 2B D4 7E
15:40:17
15:40:17 Reading object 1.0.4.6.3.255, interface ExtendedRegister
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 04 01 00 04 06 03 FF 03 00 FA C8 7E
15:40:17
15:40:17 Reading object 1.0.3.6.4.255, interface ExtendedRegister
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 04 01 00 03 06 04 FF 03 00 0A 83 7E
15:40:17
15:40:17 Reading object 1.0.4.6.4.255, interface ExtendedRegister
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 04 01 00 04 06 04 FF 03 00 DB 9F 7E
15:40:17
15:40:17 Reading object 1.0.3.6.5.255, interface ExtendedRegister
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 04 01 00 03 06 05 FF 03 00 B1 9F 7E
15:40:18
15:40:18 Access Error : Device reports Read-Write denied.
15:40:18 Reading object 1.0.4.6.5.255, interface ExtendedRegister
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 04 01 00 04 06 05 FF 03 00 60 83 7E
15:40:18
15:40:18 Reading object 1.0.3.6.6.255, interface ExtendedRegister
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 04 01 00 03 06 06 FF 03 00 7C BA 7E
15:40:18
15:40:18 Reading object 1.0.4.6.6.255, interface ExtendedRegister
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 04 01 00 04 06 06 FF 03 00 AD A6 7E
15:40:18
15:40:18 Reading object 1.0.3.6.7.255, interface ExtendedRegister
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 04 01 00 03 06 07 FF 03 00 C7 A6 7E
15:40:23 Data send failed. Try to resend 1/2
15:40:23
15:40:23 Access Error : Device reports Read-Write denied.
15:40:23 Reading object 1.0.4.6.7.255, interface ExtendedRegister
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 04 01 00 04 06 07 FF 03 00 16 BA 7E
15:40:24
15:40:24 Access Error : Device reports Read-Write denied.
15:40:24 Reading object 1.0.3.6.8.255, interface ExtendedRegister
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 04 01 00 03 06 08 FF 03 00 3E 14 7E
15:40:24
15:40:24 Reading object 1.0.4.6.8.255, interface ExtendedRegister
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 04 01 00 04 06 08 FF 03 00 EF 08 7E
15:40:24
15:40:24 Reading object 1.0.9.6.1.255, interface ExtendedRegister
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 04 01 00 09 06 01 FF 03 00 53 C4 7E
15:40:24
15:40:24 Reading object 1.0.10.6.1.255, interface ExtendedRegister
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 04 01 00 0A 06 01 FF 03 00 2E C8 7E
15:40:24
15:40:24 Reading object 1.0.9.6.2.255, interface ExtendedRegister
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 04 01 00 09 06 02 FF 03 00 9E E1 7E
15:40:25
15:40:25 Access Error : Device reports Read-Write denied.
15:40:25 Reading object 1.0.10.6.2.255, interface ExtendedRegister
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 04 01 00 0A 06 02 FF 03 00 E3 ED 7E
15:40:25
15:40:25 Reading object 1.0.9.6.3.255, interface ExtendedRegister
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 04 01 00 09 06 03 FF 03 00 25 FD 7E
15:40:25
15:40:25 Reading object 1.0.10.6.3.255, interface ExtendedRegister
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 04 01 00 0A 06 03 FF 03 00 58 F1 7E
15:40:25
15:40:25 Reading object 1.0.9.6.4.255, interface ExtendedRegister
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 04 01 00 09 06 04 FF 03 00 04 AA 7E
15:40:25
15:40:25 Reading object 1.0.10.6.4.255, interface ExtendedRegister
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 04 01 00 0A 06 04 FF 03 00 79 A6 7E
15:40:25
15:40:25 Reading object 1.0.9.6.5.255, interface ExtendedRegister
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 04 01 00 09 06 05 FF 03 00 BF B6 7E
15:40:26
15:40:26 Access Error : Device reports Read-Write denied.
15:40:26 Reading object 1.0.10.6.5.255, interface ExtendedRegister
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 04 01 00 0A 06 05 FF 03 00 C2 BA 7E
15:40:26
15:40:26 Reading object 1.0.9.6.6.255, interface ExtendedRegister
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 04 01 00 09 06 06 FF 03 00 72 93 7E
15:40:26
15:40:26 Reading object 1.0.10.6.6.255, interface ExtendedRegister
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 04 01 00 0A 06 06 FF 03 00 0F 9F 7E
15:40:26
15:40:26 Reading object 1.0.9.6.7.255, interface ExtendedRegister
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 04 01 00 09 06 07 FF 03 00 C9 8F 7E
15:40:26
15:40:26 Reading object 1.0.10.6.7.255, interface ExtendedRegister
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 04 01 00 0A 06 07 FF 03 00 B4 83 7E
15:40:27
15:40:27 Access Error : Device reports Read-Write denied.
15:40:27 Reading object 1.0.9.6.8.255, interface ExtendedRegister
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 04 01 00 09 06 08 FF 03 00 30 3D 7E
15:40:27
15:40:27 Reading object 1.0.10.6.8.255, interface ExtendedRegister
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 04 01 00 0A 06 08 FF 03 00 4D 31 7E
15:40:27
15:40:27 Reading object 1.0.14.3.0.255, interface ExtendedRegister
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 04 01 00 0E 03 00 FF 03 00 6D E2 7E
15:40:27
15:40:27 Reading object 1.0.14.6.0.255, interface ExtendedRegister
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 04 01 00 0E 06 00 FF 03 00 39 C4 7E
15:40:27
15:40:27 Reading object 1.0.15.6.0.255, interface ExtendedRegister
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 04 01 00 0F 06 00 FF 03 00 12 C0 7E
15:40:28
15:40:28 Access Error : Device reports Read-Write denied.
15:40:28 Reading object 1.0.15.6.1.255, interface ExtendedRegister
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 04 01 00 0F 06 01 FF 03 00 A9 DC 7E
15:40:28
15:40:28 Reading object 1.0.15.6.2.255, interface ExtendedRegister
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 04 01 00 0F 06 02 FF 03 00 64 F9 7E
15:40:28
15:40:28 Reading object 1.0.15.6.3.255, interface ExtendedRegister
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 04 01 00 0F 06 03 FF 03 00 DF E5 7E
15:40:28
15:40:28 Reading object 1.0.15.6.4.255, interface ExtendedRegister
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 04 01 00 0F 06 04 FF 03 00 FE B2 7E
15:40:28
15:40:28 Reading object 1.0.128.6.0.255, interface ExtendedRegister
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 04 01 00 80 06 00 FF 03 00 39 F8 7E
15:40:29
15:40:29 Access Error : Device reports Read-Write denied.
15:40:29 Reading object 1.0.128.6.1.255, interface ExtendedRegister
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 04 01 00 80 06 01 FF 03 00 82 E4 7E
15:40:29
15:40:29 Reading object 1.0.128.6.2.255, interface ExtendedRegister
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 04 01 00 80 06 02 FF 03 00 4F C1 7E
15:40:29
15:40:29 Reading object 1.0.128.6.3.255, interface ExtendedRegister
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 04 01 00 80 06 03 FF 03 00 F4 DD 7E
15:40:29
15:40:29 Reading object 1.0.128.6.4.255, interface ExtendedRegister
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 04 01 00 80 06 04 FF 03 00 D5 8A 7E
15:40:34 Data send failed. Try to resend 1/2
15:40:34
15:40:34 Access Error : Device reports Read-Write denied.
15:40:34 Reading object 1.0.129.6.0.255, interface ExtendedRegister
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 04 01 00 81 06 00 FF 03 00 12 FC 7E
15:40:35
15:40:35 Access Error : Device reports Read-Write denied.
15:40:35 Reading object 1.0.129.6.1.255, interface ExtendedRegister
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 04 01 00 81 06 01 FF 03 00 A9 E0 7E
15:40:35
15:40:35 Reading object 1.0.129.6.2.255, interface ExtendedRegister
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 04 01 00 81 06 02 FF 03 00 64 C5 7E
15:40:35
15:40:35 Reading object 1.0.129.6.3.255, interface ExtendedRegister
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 04 01 00 81 06 03 FF 03 00 DF D9 7E
15:40:35
15:40:35 Reading object 1.0.129.6.4.255, interface ExtendedRegister
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 04 01 00 81 06 04 FF 03 00 FE 8E 7E
15:40:35
15:40:35 Reading object 1.0.1.4.0.255, interface DemandRegister
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 05 01 00 01 04 00 FF 04 00 CD EF 7E
15:40:35
15:40:35 Reading object 1.0.2.4.0.255, interface DemandRegister
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 05 01 00 02 04 00 FF 04 00 B0 E3 7E
15:40:36
15:40:36 Access Error : Device reports Read-Write denied.
15:40:36 Reading object 1.0.3.4.0.255, interface DemandRegister
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 05 01 00 03 04 00 FF 04 00 9B E7 7E
15:40:41 Data send failed. Try to resend 1/2
15:40:41
15:40:41 Access Error : Device reports Read-Write denied.
15:40:41 Reading object 1.0.4.4.0.255, interface DemandRegister
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 05 01 00 04 04 00 FF 04 00 4A FB 7E
15:40:41
15:40:41 Reading object 1.0.9.4.0.255, interface DemandRegister
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 05 01 00 09 04 00 FF 04 00 95 CE 7E
15:40:41
15:40:41 Reading object 1.0.10.4.0.255, interface DemandRegister
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 05 01 00 0A 04 00 FF 04 00 E8 C2 7E
15:40:41
15:40:41 Reading object 1.0.15.4.0.255, interface DemandRegister
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 05 01 00 0F 04 00 FF 04 00 6F D6 7E
15:40:42
7E A0 12 21 02 23 1E 71 03 E6 E7 00 C4 01 C1 01 03 73 82 7E
15:40:42 Access Error : Device reports Read-Write denied.
15:40:42 Reading object 1.0.128.4.0.255, interface DemandRegister
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 05 01 00 80 04 00 FF 04 00 44 EE 7E
15:40:42
7E A0 12 21 02 23 30 0D CB E6 E7 00 C4 01 C1 01 03 73 82 7E
15:40:42 Reading object 1.0.129.4.0.255, interface DemandRegister
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 05 01 00 81 04 00 FF 04 00 6F EA 7E
15:40:42
7E A0 12 21 02 23 52 19 8B E6 E7 00 C4 01 C1 01 03 73 82 7E
15:40:42 --- Reading scalers and units end. ---
15:40:42 Reading object 0.0.98.1.0.255, interface ProfileGeneric
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 FF 03 00 18 15 7E
15:40:42 Get profile generic columns...
15:40:42
7E A0 12 21 02 23 74 2D CF E6 E7 00 C4 01 C1 01 03 73 82 7E
15:40:48 Reading object 1.0.99.10.1.255, interface ProfileGeneric
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 07 01 00 63 0A 01 FF 03 00 DB CB 7E
15:40:48 Get profile generic columns...
15:40:48
7E A0 12 21 02 23 96 31 0B E6 E7 00 C4 01 C1 01 03 73 82 7E
15:40:49 Reading object 0.0.99.1.0.255, interface ProfileGeneric
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 07 00 00 63 01 00 FF 03 00 33 11 7E
15:40:49 Get profile generic columns...
15:40:49
7E A0 12 21 02 23 B8 4D C3 E6 E7 00 C4 01 C1 01 03 73 82 7E
15:40:50 Reading object 0.0.99.2.0.255, interface ProfileGeneric
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 07 00 00 63 02 00 FF 03 00 FF 0C 7E
15:40:50 Get profile generic columns...
15:40:50
7E A0 12 21 02 23 DA 59 83 E6 E7 00 C4 01 C1 01 03 73 82 7E
15:40:50 Reading object 0.0.99.3.0.255, interface ProfileGeneric
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 07 00 00 63 03 00 FF 03 00 BB 07 7E
15:40:50
7E A0 12 21 02 23 FC 6D C7 E6 E7 00 C4 01 C1 01 03 73 82 7E
15:40:51 Reading object 0.0.98.1.0.1, interface ProfileGeneric
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 01 03 00 37 89 7E
15:40:51 Get profile generic columns...
15:40:51
15:40:51 Reading object 0.0.98.1.0.2, interface ProfileGeneric
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 02 03 00 53 66 7E
15:40:51
15:40:52 Reading object 0.0.98.1.0.3, interface ProfileGeneric
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 03 03 00 8F 3C 7E
15:40:52 Get profile generic columns...
15:40:52
15:40:52 Reading object 0.0.98.1.0.4, interface ProfileGeneric
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 04 03 00 8A B0 7E
15:40:53
15:40:53 Reading object 0.0.98.1.0.5, interface ProfileGeneric
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 05 03 00 56 EA 7E
15:40:53 Get profile generic columns...
15:40:53
15:40:53 Reading object 0.0.98.1.0.6, interface ProfileGeneric
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 06 03 00 32 05 7E
15:40:54
15:40:54 Reading object 0.0.98.1.0.7, interface ProfileGeneric
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 07 03 00 EE 5F 7E
15:40:54 Get profile generic columns...
15:40:54
15:40:55 Reading object 0.0.98.1.0.8, interface ProfileGeneric
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 08 03 00 29 15 7E
15:40:55 Get profile generic columns...
15:40:55
15:40:55 Reading object 0.0.98.1.0.9, interface ProfileGeneric
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 09 03 00 F5 4F 7E
15:40:55
15:40:56 Reading object 0.0.98.1.0.10, interface ProfileGeneric
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 0A 03 00 91 A0 7E
15:40:56 Get profile generic columns...
15:40:56
15:40:56 Reading object 0.0.98.1.0.11, interface ProfileGeneric
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 0B 03 00 4D FA 7E
15:40:57
15:40:57 Reading object 0.0.98.1.0.12, interface ProfileGeneric
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 0C 03 00 48 76 7E
15:40:57 Get profile generic columns...
15:40:57
15:40:58 Reading object 0.0.98.1.0.101, interface ProfileGeneric
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 65 03 00 1B EF 7E
15:40:58 Get profile generic columns...
15:40:58
15:40:58 Reading object 0.0.98.1.0.102, interface ProfileGeneric
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 66 03 00 7F 00 7E
15:40:58
15:40:59 Reading object 0.0.98.1.0.103, interface ProfileGeneric
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 67 03 00 A3 5A 7E
15:40:59 Get profile generic columns...
15:40:59
15:40:59 Reading object 0.0.98.1.0.104, interface ProfileGeneric
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 68 03 00 64 10 7E
15:40:59
15:41:00 Reading object 0.0.98.1.0.105, interface ProfileGeneric
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 69 03 00 B8 4A 7E
15:41:00 Get profile generic columns...
15:41:00
15:41:00 Reading object 0.0.98.1.0.106, interface ProfileGeneric
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 6A 03 00 DC A5 7E
15:41:01
15:41:01 Reading object 0.0.98.1.0.107, interface ProfileGeneric
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 6B 03 00 00 FF 7E
15:41:01 Get profile generic columns...
15:41:01
15:41:02 Reading object 0.0.98.1.0.108, interface ProfileGeneric
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 6C 03 00 05 73 7E
15:41:02 Get profile generic columns...
15:41:02
15:41:02 Reading object 0.0.98.1.0.109, interface ProfileGeneric
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 6D 03 00 D9 29 7E
15:41:02
15:41:03 Reading object 0.0.98.1.0.110, interface ProfileGeneric
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 6E 03 00 BD C6 7E
15:41:03 Get profile generic columns...
15:41:03
15:41:03 Reading object 0.0.98.1.0.111, interface ProfileGeneric
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 6F 03 00 61 9C 7E
15:41:03
15:41:04 Reading object 0.0.98.1.0.112, interface ProfileGeneric
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 07 00 00 62 01 00 70 03 00 33 53 7E
15:41:04 Get profile generic columns...
15:41:04
15:41:04 Reading object 0.0.99.17.0.255, interface ProfileGeneric
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 07 00 00 63 11 00 FF 03 00 73 A5 7E
15:41:04
15:41:05 Reading object 0.0.99.15.0.255, interface ProfileGeneric
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 07 00 00 63 0F 00 FF 03 00 8B 70 7E
15:41:05 Get profile generic columns...
15:41:05
15:41:05 Reading object 0.0.99.23.0.255, interface ProfileGeneric
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 07 00 00 63 17 00 FF 03 00 EB 9E 7E
15:41:06
15:41:06 Reading object 0.0.99.19.0.255, interface ProfileGeneric
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 07 00 00 63 13 00 FF 03 00 FB B3 7E
15:41:06 Get profile generic columns...
15:41:06
15:41:07 Reading object 0.0.99.20.0.255, interface ProfileGeneric
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 07 00 00 63 14 00 FF 03 00 27 83 7E
15:41:07 Get profile generic columns...
15:41:07
15:41:07 Reading object 0.0.99.21.0.255, interface ProfileGeneric
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 07 00 00 63 15 00 FF 03 00 63 88 7E
15:41:07
15:41:08 Reading object 0.0.99.22.0.255, interface ProfileGeneric
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 07 00 00 63 16 00 FF 03 00 AF 95 7E
15:41:08 Get profile generic columns...
15:41:08
15:41:08 Reading object 0.0.99.98.0.255, interface ProfileGeneric
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 07 00 00 63 62 00 FF 03 00 4C AD 7E
15:41:08
15:41:09 Reading object 0.0.99.98.1.255, interface ProfileGeneric
7E A0 1A 02 23 21 FE 96 7E E6 E6 00 C0 01 C1 00 07 00 00 63 62 01 FF 03 00 F7 B1 7E
15:41:09 Get profile generic columns...
15:41:09
15:41:09 Reading object 0.0.99.98.2.255, interface ProfileGeneric
7E A0 1A 02 23 21 10 E6 70 E6 E6 00 C0 01 C1 00 07 00 00 63 62 02 FF 03 00 3A 94 7E
15:41:10
15:41:10 Reading object 0.0.99.98.4.255, interface ProfileGeneric
7E A0 1A 02 23 21 32 F6 72 E6 E6 00 C0 01 C1 00 07 00 00 63 62 04 FF 03 00 A0 DF 7E
15:41:10 Get profile generic columns...
15:41:10
15:41:11 Reading object 0.0.99.98.5.255, interface ProfileGeneric
7E A0 1A 02 23 21 54 C6 74 E6 E6 00 C0 01 C1 00 07 00 00 63 62 05 FF 03 00 1B C3 7E
15:41:11 Get profile generic columns...
15:41:11
15:41:11 Reading object 0.0.99.98.6.255, interface ProfileGeneric
7E A0 1A 02 23 21 76 D6 76 E6 E6 00 C0 01 C1 00 07 00 00 63 62 06 FF 03 00 D6 E6 7E
15:41:11
15:41:12 Reading object 0.0.99.98.7.255, interface ProfileGeneric
7E A0 1A 02 23 21 98 A6 78 E6 E6 00 C0 01 C1 00 07 00 00 63 62 07 FF 03 00 6D FA 7E
15:41:12 Get profile generic columns...
15:41:12
15:41:12 Reading object 0.0.99.98.8.255, interface ProfileGeneric
7E A0 1A 02 23 21 BA B6 7A E6 E6 00 C0 01 C1 00 07 00 00 63 62 08 FF 03 00 94 48 7E
15:41:12
15:41:13 Reading object 0.1.22.0.0.255, interface IecHdlcSetup
7E A0 1A 02 23 21 DC 86 7C E6 E6 00 C0 01 C1 00 17 00 01 16 00 00 FF 08 00 18 4F 7E
15:41:13
Gurux.DLMS.GXDLMSException: Access Error : Device reports Read-Write denied.
at GXDLMSDirector.MainForm.RefreshDevice(GXDLMSMeter dev, Boolean bRefresh)
at GXDLMSDirector.MainForm.Refresh(Object sender, GXAsyncWork work, Object[] parameters)
There are lots of objects where only the logical name is implemented and there is no other data. For example, register object 1.0.21.8.0.255. There is an access right only for the logical name.
<Structure Qty="04" >
<UInt16 Value="0003" />
<UInt8 Value="00" />
<!-- 1.0.21.8.0.255 -->
<OctetString Value="0100150800FF" />
<Structure Qty="02" >
<Array Qty="01" >
<Structure Qty="03" >
<Int8 Value="01" />
<Enum Value="01" />
<None />
</Structure>
</Array>
<Array Qty="00" >
</Array>
</Structure>
</Structure>
The client application tries to read those values and you get a read-write denied error because of that.
The client application reads all the objects from the meter. You can read only values that you need and that are implemented for the meter. You can also ask if there is new firmware available for the meter where those objects are implemented.